For control valves, the valve capacity and flow characteristics are typically expressed in terms of a valve flow coefficient (Cv). This article discusses how this flow coefficient can be used to calculate the equivalent resistance coefficient, or K value, used in the Darcy equation.
The flow coefficient Cv is defined as the flow rate of 60°F water (in gpm) which can be passed by a valve with a pressure differential of 1 psid.
Similarly, the flow coefficient Kv represents the flow of water in m³/hr which can be passed by a valve with a pressure differential of 1 bar.
Kv is related to Cv by the following equation:
Kv = (0.865) Cv
The resistance coefficient (K) that is calculated or entered by the user on PIPE-FLO's valve/fitting screen is
K = f(L/D)
Where,
f = Darcy friction factor
L/D = equivalent length of a resistance to flow, in pipe diameters.
K can be calculated from the valve coefficient Cv using the following equation:
K = 891d4/(Cv2)
Where,
d = inside diameter in inches
Or, using the coefficient Kv:
K = 891d4/[(Kv/0.865)2]
If you know the Cv flow coefficient for a valve, you can either calculate a K value using the equation above, or you can use the dP Calculator feature to quickly determine the corresponding K value.
To use the dP Calculator feature, simply specify the Cv value for the flow rate (in gpm) and a pressure drop of 1 psi in the dP Calculator. The program calculates the corresponding K value.