Modeling a 3-Way Valve

  • Print this page
    Print this page
  • Remove Highlighting
    Remove Highlighting
  • Edit this Article
    Edit this Article
  • Export to PDF
    Export to PDF
PIPE-FLO does not have a native 3-way control valve.  However, the functionality of a 3-way control valve can be modeled using a combination of two Flow Control Valves.

To model a 3-way valve in PIPE-FLO, you can use a combination of two Flow Control Valves (FCVs).  The example below will demonstrate how to do this.

Figure 1 shows a section of piping where a 3-way control valve will be used.



The total flow into the section is 400 cfm and we want the flow to split 75%/25% between the AHU branch and the bypass branch.  There are two options for accomplishing this.

The first option is shown in Figure 2 below:



The flow rate is set in each branch (75% of the total flow through the AHU branch and 25% of the total flow through the bypass branch).  Note that the total flow into the section will be equal to the sum of the set FCVs (300 cfm + 100 cfm = 400 cfm).

The second option is shown in Figure 3 below:



The total flow rate into the section is set with an FCV set to 400 cfm.  The flow is then split between the AHU and bypass branches by specifying the flow rate with an FCV in one of the branches (in this example, 300 cfm in the AHU branch).  The flow rate through the bypass line will then be equal to 100 cfm (400 cfm – 300 cfm = 100 cfm).

NOTE:  If the results calculated for the FCV in the AHU branch turn out to be "Invalid," i.e. there is pressure gain across the valve instead of an pressure drop, then you should remove the FCV from that branch and instead install the FCV in the bypass branch at 100 cfm.  See Knowledge Base, "Finding the Most Hydraulically Remote Loop."

Related Articles

Attachments

No attachments were found.

Article Details

Last Updated
11th of May, 2009

Version
2005, 2007, 2009

Program
Flow of Fluids, PIPE-FLO Lite, PIPE-FLO Professional

Would you like to...

Print this page Print this page Email this page Email this page Remove Highlighting Remove Highlighting Edit this Article Export to PDF

User Opinions (0 votes)

No users have voted.

How would you rate this answer?



Thank you for rating this answer.

Visitor Comments

No visitor comments posted. Post a comment

Post a comment

To post a comment for this article, simply complete the form below. Fields marked with an asterisk are required.

Entering your email address is optional. It will not be displayed on this page, but may be used by our staff to contact you regarding your comment.

For technical support, please do not use this form. Use our Web Support Form or email solutions@eng-software.com, instead.

   Name:
   Email:
* Comment:
* Enter the code below: