There are several ways to model a sprinkler system or a system with nozzles in PIPE-FLO.

Sprinklers, fire suppression nozzles, and spray nozzles are typically characterized by a Discharge Coefficient which some nozzle manufacturers represent with the letter K, used in the following equation:





This conflicts with the way PIPE-FLO uses the letter K, which is used to represent the Resistance Coefficient of valves and fittings. This inconsistent use of nomenclature has resulted in confusion when modeling a spray nozzle within PIPE-FLO. For a spray nozzle, increasing the value of the discharge coefficient increases the flow rate through the nozzle, but when using the resistance coefficient to describe a spray nozzle, increasing the resistant coefficient decreases the flow rate through the nozzle.

The nozzle discharge coefficient is also equivalent to the flow coefficient (Cv) when used with water at 60 degF (SG=1.0), using U.S. units (N1=1.0), and no piping fittings (Fp=1.0), as shown in the following equation for Cv for a control valve:





When using the Darcy Weisbach calculation method, the nozzle can be modeled as a: 
1. component
2. fixed Cv 
3. equivalent fixed resistance (K) fitting in a pipeline

When using the Hazen Williams calculation method, the nozzle should be modeled as a component with a curve. The fixed Cv and fixed resistance cannot be used because dP is calculated using Q2 for these methods, whereas Hazen Williams uses Q1.85 to calculate the head loss and dP.

Consider the following graph given by a nozzle manufacturer for a range of available nozzles:



Nozzle as a Component (Darcy or Hazen-Williams Method)
To model the nozzle as a component with a Knozzle=7.2, several data points can be generated for the component dialog box data table using the nozzle equation, Q=K(dP)0.5 as shown below (these values were calculated in Excel). The data points can be confirmed on the manufacturer's graph.



The nozzle component has an outlet pipe of very short length (0.001 ft) with a spray boundary pressure of 0 psig. Now PIPE-FLO will use the component data to interpolate between values for any flow rate that is calculated for the component, as shown below for the component with a flow of 45 gpm. The calculated dP can be compared to the manufacturer's graph at 45 gpm.



Nozzle as a Fixed Cv (Darcy Method ONLY)
The nozzle can also be modeled as a fixed Cv installed as a fitting in a pipeline of very short length, as shown below.



Again, as the flow rate changes, the correct differential pressure will be calculated, as shown below and confirmed in the manufacturer's graph above. Conversely, as the inlet pressure of the nozzle changes, the correct flow rate will be calculated.



Nozzle as a Fixed K (resistance) (Darcy Method ONLY)
Modeling the nozzle as a fixed resistance (K) requires the use of the dP calculator and taking a data point off the graph or calculating the data point. In the dialog box below, a data point of 50.9 gpm and 50 psig is used to calculate the resistance coefficient, K=23266.



The use of the fixed K can be confirmed by comparing another point on the manufacturer's curve, in this case at 55 gpm, PIPE-FLO calculates a dP of 58.38 psi. This corresponds to the value on the graph.



Modeling a Fire Suppression System
Modeling nozzles as components can be seen in the following fire suppression system in which PIPE-FLO is used to size the fire pump to ensure at least 20 gpm at each nozzle (discharge coefficient = 3.2 from the manufacturer's graph above). Each nozzle is modeled as a component using calculated data points from the nozzle equation. The Darcy calculation method is used. The figure below shows a scenario in which the entire system is activated on both floors. The pump was selected based on a design point of 500 gpm and 110 ft of head.



Below is the same system except that the nozzles are modeled as fixed Cv fittings in the pipeline. Flow rates are caparable to the system above, with the exception of a slight variation due to the linear interpolation method used in the components above.


Here is the same system using components to model the nozzles and using the Hazen-Williams method to calculate the head loss. In this situation the flow rates and dP are comparable to the two models above, but this is highly dependent on the Hazen-Williams "C" factor, the pipe sizes, and the use of water at 60 degF.

Article Details

Last Updated
15th of September, 2009

Version
2005, 2007, 2009

Program
Flow of Fluids, PIPE-FLO Lite, PIPE-FLO Professional

Would you like to...

Print this page Print this page Email this page Email this page Remove Highlighting Remove Highlighting Edit this Article Export to PDF

User Opinions (5 votes)

100% thumbs up 0% thumbs down

How would you rate this answer?



Thank you for rating this answer.

Visitor Comments

  1. Comment 1 Posted by: khaled

    thanks

  2. Comment 2 Posted by: krishnakumar.A

    Thanks for the information you provided. Regards, Krishnakumar.A

Post a comment

To post a comment for this article, simply complete the form below. Fields marked with an asterisk are required.

Entering your email address is optional. It will not be displayed on this page, but may be used by our staff to contact you regarding your comment.

For technical support, please do not use this form. Use our Web Support Form or email solutions@eng-software.com, instead.

   Name:
   Email:
* Comment:
* Enter the code below: