Static Head in Systems with Varying Fluid Temperatures

  • Print this page
    Print this page
  • Remove Highlighting
    Remove Highlighting
  • Edit this Article
    Edit this Article
  • Export to PDF
    Export to PDF
Q.  What is static head and how is the static head calculated for a system that contains a fluid at different temperatures?

A.  The static head of a system is that portion of the pump’s Total Head that must be added to the fluid before a single drop of fluid will move in the system. It is the amount of energy, or head, which is used to overcome the pressure and elevation differences in the piping system. It can be calculated using the following equations:



where:  static, elevation, and pressure head are in units of feet of fluid
pressure in units of lb/in2 (psi)
density (ρ) in lb/ft3 of the fluid in the pump

If the system contains fluids at different temperatures the fluid density will vary. So which fluid density should be used in the equation:  the density of the hotter fluid, the colder fluid, or an average density? How much difference does it make? Does it affect the differential pressure head or differential elevation head component of static head?

At first glance , based on the equations, it appears that the fluid density will affect the differential pressure head component. But the pressure difference between the two tanks has to be overcome regardless of the densities of the fluid between the two tanks. And since static head is a portion of the Total Head at the pump, the density of the fluid in the pump is used in the pressure head component of the static head calculation.

It is actually the differential elevation head component that is affected by the fluid density. A column of fluid of a given height will equate to a pressure at the bottom of the column, which will be different compared to the same column of fluid with a different density. It is the differential elevation head component that must be adjusted to ensure the terms of elevation head are related to the fluid at the pump.

Consider the following open systems in which water is pumped from a supply tank (bottom elevation = 0 ft, liquid level = 10 ft, and surface pressure = 0 psig) to an elevated product tank (bottom elevation = 150 ft, liquid level = 10 ft, and surface pressure = 10 psig).



The first system is pumping water at 60°F and the second system has a heat exchanger at the 25 ft elevation that heats the water up to 200°F.

The calculation for static head in the first system is:



This value of static head can be confirmed using PIPE-FLO by plotting the System Resistance Curve and setting the flow rate to zero:



In the second system, the water from the liquid surface in the supply tank to the inlet of the heat exchanger (at 25 ft elevation) has a density of 62.37 lb/ft3, but the water from the heat exchanger to the liquid surface in the product tank has a density of 60.11 lb/ft3. To calculate the static head requires adjusting the elevation head between the heat exchanger and product tank by the ratio of the fluid densities to put it in terms of head at the pump:



This value of static head can also be confirmed using PIPE-FLO:



The difference in the calculated static head between the two systems may or may not be significant enough to justify calculating the density correction in the system, depending on the degree of accuracy required in the calculations and the magnitude of the difference between the fluid densities.

Related Articles

Attachments

No attachments were found.

Article Details

Last Updated
27th of December, 2010

Would you like to...

Print this page Print this page Email this page Email this page Remove Highlighting Remove Highlighting Edit this Article Export to PDF

User Opinions (2 votes)

100% thumbs up 0% thumbs down

How would you rate this answer?



Thank you for rating this answer.

Visitor Comments

No visitor comments posted. Post a comment

Post a comment

To post a comment for this article, simply complete the form below. Fields marked with an asterisk are required.

Entering your email address is optional. It will not be displayed on this page, but may be used by our staff to contact you regarding your comment.

For technical support, please do not use this form. Use our Web Support Form or email solutions@eng-software.com, instead.

   Name:
   Email:
* Comment:
* Enter the code below: