Pump curves: accounting for suction / discharge elevation difference

  • Print this page
    Print this page
  • Remove Highlighting
    Remove Highlighting
  • Edit this Article
    Edit this Article
  • Export to PDF
    Export to PDF
Question:
There are often cases where the centerlines of the suction and discharge from a given pump are not on the same level. Some cases can be more significant than others. When the manufacturers create their curves, are they accounting for this change in elevation in the data?

Answer:
The Hydraulic Institute standard asks the manufacturers to restate the total head relative to the centerline of the pump. So, if the manufacturer has gages at the suction and discharge flanges, they are supposed to adjust for the location of these gauges relative to the centerline.
 
That being said, there is no guarantee that all manufacturers make this adjustment correctly. If, for example a manufacturer were only using a discharge gauge in their test, they would be mixing up total head with total discharge head which would overstate the pump’s actual performance.
 
If you have any doubts, the best bet is always to contact the manufacturer of the pump you are considering for your application to verify what method they use to gather their data.


Guest Expert:
This Ask an Engineer answered by Pump Consultant, Michael Volk, P.E. President of Volk & Associates, Inc. Author of the reference,
Pump Characteristics and Applications, Second Edition, published by CRC Press.

To read more about Michael Volk, click here.




Related Articles

Attachments

No attachments were found.

Article Details

Last Updated
21st of October, 2011

Would you like to...

Print this page Print this page Email this page Email this page Remove Highlighting Remove Highlighting Edit this Article Export to PDF

User Opinions (2 votes)

100% thumbs up 0% thumbs down

How would you rate this answer?



Thank you for rating this answer.

Visitor Comments

  1. Comment 1 Posted by: Jack Claxton

    The calculation of pump total head is a very basic, straightforward procedure clearly defined in the the Hydraulic Institute pump test standard (available from www.pumps.org). I would doubt that many, if any, established pump manufacturers would get this wrong. The reason for the question is not provided, however, if it is because of an observed variance of pump performance as measured in the field as compared to the factory test curve provided by the manufacturer, the explanation of the variance often lies in the limitations of typical field test system conditions and instrumentation. Regards, Jack Claxton, P.E. Vice President, Engineering Patterson Pump Company Toccoa, GA 30577

Post a comment

To post a comment for this article, simply complete the form below. Fields marked with an asterisk are required.

Entering your email address is optional. It will not be displayed on this page, but may be used by our staff to contact you regarding your comment.

For technical support, please do not use this form. Use our Web Support Form or email solutions@eng-software.com, instead.

   Name:
   Email:
* Comment:
* Enter the code below: